The use of a heating curve offers more flexibility than a constant temperature. Two points on the heating curve can be adjusted through HeishaMon. This allows you to work with the curve, and if the target temperatures for both points on the curve are the same, you achieve a constant heating temperature. |
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
I'm trying to set the heating temperature but I fail. According to the documentation there is MQTT command to do it:
SET5 | SetZ1HeatRequestTemperature | Set Z1 heat shift or direct heat temperature | -5 to 5 or 20 to max
It works fine as shift in the range -5...5, but when I try to set fixed 30 degree it always goes back to -5...5 range.
Are there any other settings enabling flat temp value? Im using Curve at the moment, so maybe I need to disable it first? But how?
Beta Was this translation helpful? Give feedback.