#2257 (comment) describes how OTGW handles thermostatic control |
Beta Was this translation helpful? Give feedback.
-
Another note: While my setup seems to ignore/override the |
Beta Was this translation helpful? Give feedback.
-
Looking into the code, the @oliof, is one solution to disable the onboard RC310 thermostat? I don't know if there is an option in the device to make it a slave device? I can't see any way of having EMS-ESP take over and be the master "simulated" thermostat in the chain. |
Beta Was this translation helpful? Give feedback.
-
Looking at the installation manual for the RC310, you can choose one existing thermostat, but not no thermostat to take over control. That's why I started thinking about integrating SAT like the Remote Thermostat, which takes over from the RC310 as a simulated RC200/RC100H. Current deliberation confuses me more about whether EMS-ESP or SAT needs to do the RCxxx emulation to allow for cleaner integration. |
Beta Was this translation helpful? Give feedback.
-
Alright, that makes sense and is a bit of a bother for people that worry about replacing/disconnecting the thermostat on their boiler (may require some reconfiguration to avoid the boiler going into error mode?). I think this is an important tidbit I missed before that needs to be documented on the SAT side. |
Beta Was this translation helpful? Give feedback.
-
The current beta implementation of SAT works to some extent, for example on boilers that speak EMS(plus) but don´t have a thermostat like the RC3*0 or a (dummy) remote thermostat installed. With those boilers in the mix, there is room for error:
To ensure that SAT actually has control over the boiler, it should be integrated like a remote thermostat so that the boiler expects control from that.
There may still be some control gaps -- in my case for example the boiler ignored
force heating off
and a low burner power setting, which usually is enough to disable the boiler. My assumption is that either the thermostat setting, or the outside temperature input, cause the RC310 on my boiler to ignore/override the commands SAT sends.In addition, there needs to be more documentation about
Beta Was this translation helpful? Give feedback.